Within motors, two very different types of resistance are evident. The resistance of the windings is measured with a normal multimeter. But what is insulation resistance, and how is it measured?


Technical Article January 16, 2024 by Gunner Scott

In the dynamic landscape of industrial machinery, electric motors, acting as workhorses, silently drive essential processes, making them indispensable components in manufacturing, energy production, and beyond. However, like any mechanical device, electric motors are not immune to the wear and tear of time and operational stresses. To safeguard their reliable performance and longevity, engineers turn to a critical diagnostic procedure known as "megger testing."

This article delves into the significance of insulation resistance, provides a step-by-step guide on how to megger a motor, explores the tools integral to the process, and sheds light on the diverse applications of this indispensable technique.

 

Importance of Insulation Resistance

Insulation resistance plays a pivotal role in maintaining the integrity of a motor's electrical system. The insulation materials within a motor, such as winding insulation and cable insulation, prevent unintended electrical contact and leakage current to the outside casing. Over time, environmental factors, temperature fluctuations, and operational stressors can degrade this insulation, leading to a decline in performance and, in extreme cases, catastrophic failure.

 

Are you a motor troubleshooting expert? Quiz yourself with our (no pressure) worksheet!

 

Megger testing is specifically designed to measure the resistance of the insulation, helping identify potential issues before they escalate. By assessing insulation resistance, engineers can gain insights into the motor's overall health and predict potential faults. Regular megger testing is a proactive approach to prevent unexpected downtime, extend motor life, and enhance overall system reliability.

 

Electrician using a megaohmmeter (megger)

Figure 1. Operator performing a megohmmeter test on equipment for insulation troubleshooting. Image used courtesy of Fluke

 

Tools Used in Megger Testing

Megger instruments (an abbreviation of the more formal ‘megaohmmeters’) are specialized devices designed for insulation resistance testing. These tools are available in various types, each catering to specific applications and voltage ranges. Some common types of meggers include:

 

Handheld Meggers

Portable and user-friendly, handheld meggers are suitable for routine insulation resistance testing. They are often used in field applications where mobility is essential. Even today, these instruments often include a crank handle and analog display, removing any need for batteries.

 

Motorized Meggers

Motorized meggers are equipped with additional features such as automatic voltage regulation and data logging. These instruments are suitable for more comprehensive testing and are often employed in laboratory or workshop settings.

 

Digital Megohmmeters

Digital megohmmeters provide precise readings and are often equipped with advanced features such as data storage, Bluetooth connectivity, and programmable test sequences. They are ideal for in-depth insulation resistance analysis.

 

High-Voltage Meggers

For high-voltage applications, specialized high-voltage meggers are employed. These instruments can generate test voltages of several kilovolts, making them suitable for testing large motors and high-voltage systems.

 

A handheld digital megaohmmeter

Figure 2. Example of handheld megger design in operation. Image used courtesy of Megger

 

How to Megger a Motor

Megger testing involves applying a high-voltage DC potential to the motor's insulation system and measuring the resulting current flow. This test provides a quantifiable measure of the insulation resistance, typically expressed in hundreds of megaohms, or even gigaohms.

A standard multimeter is not suitable for this application because the voltage applied from the batteries will fail to deliver a current that can even be measured within the standard ohmmeter’s operating range (usually only up to a few 10s of megaohms).

To perform a megger test on a motor, follow these general steps:

  • Prepare the Motor: Before starting the test, ensure the motor is de-energized and properly isolated. Disconnect the motor from the power source and discharge any stored electrical energy (many 1-phase AC motors have a starting capacitor). A disconnect or motor starter can be an easy location to disconnect supply power.
  • Select the Megger Instrument: Choose an appropriate megger instrument based on the motor's voltage rating. Meggers are available in various voltage ranges, and selecting the correct one is crucial for accurate results.
  • Connect the Megger: Connect the megger’s leads to the motor input terminals. The positive lead is connected to the motor's winding, while the negative lead is connected to the motor's frame or ground. This configuration allows the megger to measure the insulation resistance from the winding to the ground. Figures 3 and 4 diagrammatically demonstrate the proper layout for a megger test for both an AC and DC motor, respectively.

 

Connecting a megger to a 3-phase AC motor

Figure 3. Typical megger testing layout of AC Motor and associated starting equipment. Image used courtesy of the Control Automation engineering team

 

Connecting a megger to a DC motor

Figure 4. Typical megger testing layout of DC motor. Image used courtesy of the Control Automation engineering team

 

  • Apply Test Voltage: Set the megger to the desired test voltage, typically ranging from 500 to 5000 volts, depending on the motor's specifications. Apply the test voltage and allow sufficient time for the readings to stabilize.
  • Record and Analyze Results: Record the insulation resistance value displayed on the megger. A higher resistance value indicates better insulation integrity. Compare the obtained value with the motor's specifications or industry standards to assess the insulation condition.
  • Interpret Results: Analyze the results in the context of the motor's operating conditions. A significant decrease in insulation resistance may indicate moisture ingress, contamination, or insulation breakdown. Further investigation or corrective measures may be necessary based on the findings.

 

Applications of Megger Testing

While megger testing is essential for proper motor maintenance, megger testing is a versatile diagnostic technique with applications across various industries. Some additional applications include:

 

Transformer Testing

Transformers are a key step in the power distribution process. Megger testing is used to assess the insulation resistance of transformer windings, ensuring their reliable and safe operation.

 

Cable Testing

Megger testing is applied to assess the insulation integrity of power cables. This is particularly important in industries where cable failures can lead to significant disruptions and safety hazards.

 

Switchgear Testing

Switchgear, which controls the flow of electrical power, undergoes regular megger testing to ensure the insulation resistance of its components, preventing electrical faults and ensuring operator safety.

 

Generator Testing

Generators, whether used in power plants or backup systems, undergo megger testing to verify the insulation resistance of their windings and detect potential faults.

 

Control Panel Testing

Megger testing is performed on control panels and distribution boards to ensure the insulation resistance of electrical circuits, promoting the safety and reliability of control systems.

 

What it Means to Megger a Motor

Insulation resistance testing, commonly known as megger testing, is a fundamental aspect of maintaining the reliability and performance of electric motors and associated electrical systems. By regularly assessing the insulation integrity, engineers can identify potential issues before they escalate, preventing costly downtime and equipment failures.

The process of megging a motor involves the application of high-voltage DC potential and measuring the resulting current flow. With the use of specialized megger instruments, ranging from handheld devices to high-voltage meggers, this diagnostic technique has become accessible and efficient.

Megger testing finds applications across diverse industries, from motor and transformer testing to cable and switchgear assessments. Its proactive nature allows for preventive maintenance, contributing to the overall reliability of electrical systems.

In conclusion, understanding how to megger a motor is essential for any maintenance or reliability engineer involved in electrical systems. Incorporating regular megger testing into a comprehensive maintenance program is a key step toward ensuring the longevity and dependable operation of electric motors and associated equipment.

 