Circuit Failure Analysis

DC electrical fault analysis is surprisingly one of the simplest processes in electronics. Most failures are limited to three problems: open circuit, short circuit, or unwanted change in resistance.
Perhaps the most valuable skill an instrument technician can possess is the ability to efficiently diagnose malfunctioning systems: determining in as short a time as possible the cause of a system’s malfunction. Since most instrumentation and control systems are based on electricity, a solid understanding of electrical faults is the foundation of this skill set. In this section we will explore the two basic types of electrical faults (opens and shorts) and analyze their respective effects in DC circuits.
Electrical Faults - Opens and Shorts
An open is an electrical fault whereby the pathway for electrical current is broken, thus preventing the passage of current. A short is an electrical fault whereby two points in a circuit that are supposed to be separated are joined together by a conductive pathway. It should be noted that this definition for the word “short” both is technical and specific. This is important to understand, as many people tend to use the word “short” to refer to any electrical problem in general. In technical parlance, a “short” fault is the exact opposite of an “open” fault, and should never be confused one for the other.
DC Circuit Failure Analysis
Let us examine the effects of both faults in a simple two-resistor DC circuit. We will begin with an analysis of the circuit in a healthy condition, showing all values of voltage and current:
Being a series circuit, the current is the same through all components while the two loads’ voltage drops add to equal the source voltage.
Open Circuit Fault
Now suppose resistor \(R_1\) fails open. We know that a continuous electric current is able to exist only where there is a continuous path for that current. If a component fails open, the continuity of the circuit will be broken, and current must halt. Since this is a series circuit, if current halts in one location it must likewise halt in all locations:
We would still expect to measure 15 volts between test points A and B because it is the nature of a voltage source to maintain a constant voltage across its terminals (i.e. to maintain the same amount of energy difference per unit charge from one side to the other). We may apply Ohm’s Law to calculate the voltage across the healthy resistor \(R_2\): since \(V = IR\) and \(I = 0\), we may safely conclude that \(V = 0\) for resistor \(R_2\).
Unfortunately, we cannot apply Ohm’s Law to the failed resistor \(R_1\) since the resistance of any failed-open component is infinite. Infinitudes do not lend themselves to arithmetic calculations (how much is zero times infinity?), and so we must find some other way to determine the voltage dropped across the open \(R_1\). Here we find that Kirchhoff’s Voltage Law applies very nicely: if we know that the algebraic sum of all voltages in a loop must equal zero, and we know all but one of the voltages in the loop BACDB, we may calculate the last voltage by simple addition and subtraction:
Path | Voltage gain/loss | Reason |
B to A | +15 volts | Source voltage value |
A to C | \(-\)15 volts | Necessary to satisfy KVL |
C to D | 0 volts | These points are equipotential |
D to B | 0 volts | Ohm's Law: V = 0 A \(\times\) 500 \(\Omega\) |
BACDB | 0 volts | KVL sum = 0 |
Clearly, the voltage between points A and C (across the failed-open \(R_1\)) must be \(-15\) volts in order to satisfy Kirchhoff’s Voltage Law. The negative sign of \(V_{AC}\) tells us that point C must be at a lesser potential than point A (i.e. A is positive and C is negative).
Short Circuit Fault
Let us suppose now resistor \(R_1\) fails shorted. This means its two terminals are now directly connected to each other rather than being separated by 1000 ohms of electrical resistance. In other words, the two terminals of resistor \(R_1\) have been made equipotential by the shorted fault. By extension, this forces points A and C to be equipotential as well. Since points C and D are already equipotential to each other by virtue of the wire connecting them, points A through D must now be equipotential.
If points A through D are all equipotential, it means the right-hand terminal of resistor \(R_2\) is directly connected to the positive terminal of the 15 volt source. The left-hand terminal of \(R_2\) is already equipotential with the negative terminal of the source. This means the shorted fault at \(R_1\) has placed the full source potential across resistor \(R_2\). An analysis using Kirchhoff’s Law confirms this:
Path | Voltage gain/loss | Reason |
B to A | +15 volts | Source voltage value |
A to C | 0 volts | Shorting points makes them equipotential |
C to D | 0 volts | These points are equipotential |
D to B | \(-\)15 volts | Necessary to satisfy KVL |
BACDB | 0 volts | KVL sum = 0 |
The negative sign of \(V_{DB}\) tells us that point B must be at a lesser potential than point D (i.e. D is positive and B is negative). Calculating the amount of current in this circuit is now a simple matter of applying Ohm’s Law to resistor \(R_2\). Given a 15 volt potential across it and 500 ohms of resistance, the current is equal to 30 milliamps:
Determining Open Fault and Short Fault Symptoms
All DC circuit fault analysis reduces to these simple principles: open faults directly affect current by interrupting the continuity of the circuit, while shorted faults directly affect voltage by making points equipotential to each other that were not equipotential before. The rest is merely applying Kirchhoff’s and Ohm’s Laws to determine the consequences of the fault throughout the circuit.
REVIEW:
-
Open circuits exist when a wire or device is broken, acting like a permanently open switch.
-
Open circuit breaks are identified by the loss of the entire voltage across this near-infinite series resistance.
-
-
Short circuits reduce the resistance of one or more components to zero, lowering the overall circuit resistance and increasing current.
-
Short circuit points are identified by the loss of zero volts across a component which should normally have a finite voltage drop.
-
Alternatively, short circuits can be identified by the loss of the entire source voltage across the remaining resistors.
-